I have a 1995 Lennox Value series gas heater and Air conditioner. Laterly, the burner doesn't ignite when it is off for a while. I had to cycle the thermostat power few time, then it will ignite, but still take few time. When the burner is running for a while, then it ignites right away the first time.
I had a service tech looked at it, he said that the circuit board is bad and needed to be replace to get rid of this problem.
My Lennox model is 80MGF4X-75A-5, serial# is 6396J15448.
Any suggestions? Thank you very much for your help.
First have the burners removed and thoroughly cleaned. Debris inside the burners especially in the area of the carry over wings become clogged with lint. The first burner or two may be lighting, but because the flame does not reach the end burner with the flame sensor the control board will cycle the burner system off. Has the draft been checked with an inclined manometer, electronic manometer, or magnehlic gauge. The draft pressure switch must first close for the circuit to start the igniter and open the gas valve. debris in the vent system can cause this problem. If the problem is the control also recommend that you also get the dual rod flame sensor kit if it has not already been installed. Helps eliminate nuisance lock outs from low flame sensor current. Product Name: Dual rod flame sensor upgrade kit, 62K5001
I am having a problem with my G23 series Lennox Furnace. It works fine most of the time but every now and then it won't run when the thermostat tells it to. Turning the power off to the furnace for a second or two then back on again makes it run most of the times. I also saw a detailed solution in a different board. http://www.bobvila.com/wwwboard/messages/243884.html Do you agree with the solution? I know I cannot take care of it myself. So is it better to replace the IPIC. IF it has to be replaced what is it that needs to be ordered. My Lennox furnace details are Model No. G23Q5/6 -150 -2 Serial Number - 5896F 6500S
I am having a problem with my G23 series Lennox Furnace. It works fine most of the time but every now and then it won't run when the thermostat tells it to. Turning the power off to the furnace for a second or two then back on again makes it run most of the times. I also saw a detailed solution in a different board. http://www.bobvila.com/wwwboard/messages/243884.html Do you agree with the solution? I know I cannot take care of it myself. So is it better to replace the IPIC. IF it has to be replaced what is it that needs to be ordered. My Lennox furnace details are Model No. G23Q5/6 -150 -2 Serial Number - 5896F 6500S
Replace the control with the 53L90. Lennox has replaced the Johnson Control with one manufactured by Honeywell. It contains the ignition control, a new flame sensor and hardware to mount it. Bottom line on this is litigation. If I were to resolder the connections and the control then failed causing either minor or major damage as the last person working on it I would be responsible. The lawyers would ask how much training I had in repairing these controls, does the control manufacturer authorize such repairs, and on and on. It is just not worth it.
Hi, I have had a similar problem. I have a 1993 Lennox G20RE series furnace. One year after I got the furnace, my repairman had to replace the igniter control module with a new one. That unit has worked for about 11 years. But now, I am having problems with the furnace igniting intermittently. I would guess it is the igniter system. Someone mentioned a Honeywell unit. Could an amateur like myself replace the current igniter system with this new Honeywell unit? Thanks,
We also have a value series gas furnace that won't ignite. We have changed the igniters to the dual ignite. I was working but we constantly have to clean the igniters (even the new ones) and now it has stopped igniting all together. We have been told the mother board needs to be replaced. Can it be something else? Everything else seems to be working fine.
It could be the circuit board... but I would sure have them check the pressure switch on the induced draft blower before they order...that gets missed a lot.
Also, make sure you have a very good cabinet ground (earth ground) going to the furnace and that the ground wire is installed between the cabinet ground and the burner deck.